by Goeran Eggers (TRINAMIC) » 07 Nov 2011, 10:56
Dear Gavy,
in principle differential S/D signals are no problem. You can use one one of each signal pairs and connect them to the Enable and Step signal inputs (and just ignore the other signals).
But:
- the voltage difference between low and high level of the signals should be high enough (close to +5V or higher) in order to drive the opto-coupler
- you should have an additional common supply voltage which is close to the high level of theses signals. This voltage has to be connected to the "COMMON" input
If the voltage levels are high enough but, a common supply voltage is missing the following might work:
Connect signals:
- connect "DIR-" (differential output, inverted signal) of the controller to "DIRECTION" input of the TMCM-1060
- connect "STEP-" (differential output, inverted signal) of the controller to "STEP" input of the TMCM-1060
"generate" common input voltage
- connect "DIR-" (differential output, inverted signal) of the controller via a schottky (low drop) diode to the "COMMON" input of the TMCM-1060
- connect "DIR+" (differential output, non-inverted signal) of the controller via a schottky (low drop) diode to the "COMMON" input of the TMCM-1060
- you may place an additional capacitor behind the two diodes at the "COMMON" input
-> this way there should always be a positive supply connected to "COMMON"
Hope this helps